Take the 2-minute tour ×
Server Fault is a question and answer site for professional system and network administrators. It's 100% free, no registration required.

My sever needs 10Kva UPS but i have connected all the six rack severs+ SAN storage in a 5 Kva UPS...power shut down is 99.9% impossible..but still wat would happen if power goes off ! suggest and advice..!

share|improve this question
    
If your UPS are under powered you may trip the circuit breaker or you may damage equipment. –  Zoredache Mar 9 '10 at 18:05
add comment

1 Answer

Well, since you need 10Kva, and only have 5Kva UPS, you're servers are going to go down ... hard. The only real solution is to get a properly sized UPS.

share|improve this answer
add comment

Your Answer

 
discard

By posting your answer, you agree to the privacy policy and terms of service.