We have two UPS units in our data center. All of our servers and network equipment have dual redundant supplies, one plugged into each UPS. We recently had a failure of one UPS. The servers and network hardware were not affected because they were still being powered by the other UPS. However, we have some equipment that only have a single source of power with no option for redundant power. They lost power during this failure. Are there any devices that could allow devices like this to plug into two power sources for redundancy?

share|improve this question
    
I'd like to know this too. Some expensive network equipment comes with only one power supply :-/ –  dunxd Sep 27 '10 at 14:52
    
one word of advice that I'm sure you know already but I'd rather you know twice than not at all is that you need to ensure that both of your UPSs in the scenario you describe above are connected to the same electrical phase. Failing to do this will put your equipment and safety at risk. –  Chopper3 Sep 27 '10 at 15:35
    
@Chopper3, there is equipment available for doing this safely, despite the sources being fed from different electrical phases. The APC Transfer Switches will do exactly this by detecting when one source fails and quickly switching to another source. –  Sean Reifschneider Dec 13 '10 at 7:12

3 Answers 3

up vote 5 down vote accepted

Something list this APC Rack-mount Transfer Switch, maybe?

share|improve this answer
    
Perfect, thanks! –  obsidian Sep 27 '10 at 14:51
    
Your answer would be better if you gave a short description of what "this" is. Links decay. –  Dennis Williamson Sep 27 '10 at 14:55
    
Updated answer to include description of "this". –  TCampbell Sep 27 '10 at 14:57

Yes - a transfer switch - something like this or this

share|improve this answer

Some equipment I've dealt with before, you could remove the standard AC power supply, drop in a DC supply, then use a special splitter cable to attach that to more than one external AC to DC power supplies.

share|improve this answer
    
A description of "some equipment" would be nice; this is too vague otherwise. –  Mei Nov 11 '11 at 20:59
    
In this case it was all Cisco equipment. –  Brian Knoblauch Nov 14 '11 at 13:59