I've previously had to deal with powering off a data center with well over 200 systems, but without the move part. (To install a load transfer switch and to replace all of the batteries in the UPS room) I'll have to deal with moving between buildings sometime next year, though, but it's only 7 racks.
So, on top of what others have already said:
Of course, there's the backups, and
testing the backups. If you can, get
extra hardware, or repurpose whatever
test hardware so you can pre-position
critical services. (DNS, NTP,
syslog, anything else other systems
might need to come back up.) You
might also considering boxing up
whatever spares you have (cables,
drives, power supplies, etc) so
they're ready to ship, too.
Have all of the power tested before you're ready to move -- and make sure it's not just 'yes, the hot's hot', as your UPSes will balk at an open neutral, and then you've got to try to track down an emergency electrician.
If you have a lot of network connections going between racks (eg, to a single 'networking rack', consider having all of the network drops already prepared for the racks ... punch down (and test!) patch panels that you can slap in the rack and cable up to, and avoid dealing with the long network runs on top of everything else.
Look for single points of failure, and make sure you have a spare or can bypass it --
we had our terminal server die, which
meant we had to take the few wyse
terminals we had to build two crash
carts that we could drag from server
to server to check on the ones that
weren't coming up clean.
Make sure you have all of your
vendor's support numbers available.
If you have a high level support
contract, you might see if they'll
send out an engineer with spare parts
to be there in case things go wrong. Some might even require their personnel to be there to oversee things or they'll void your support contract.
Recruit a manager (someone who's got a vested interest with enough clout in the company, but isn't directly needed for bringing everything back up) to be in charge of
keeping other management folks from
bugging your team. They don't seem
to get that when you're trying to
deal with things that went wrong,
every time they ask you how long it's
going to take, they're breaking your
concentration. The manager can also be responsible for making sure that people have food and their preferred caffeine source, and be able to pull people out when they're dead on their feet and need they're doing more harm than good (although, that take-away's from a mail system rebuild with some of us working 12-16hr days for 16 days straight)
If your sysadmins have long commutes, get the company to rent some nearby hotel rooms for them so you're not losing 2-3 hrs per day to commuting. (again, from the mail system rebuild).
If you're really paranoid, I'd ask
for two moving trucks or take two trips, and don't
transport primary systems with their
backups. Or if time's an issue,
break down the most critical racks
first, and send them out in the first
trip while someone else finishes
breaking down the less critical racks
for a second trip.
For the dollies, the moving company
should be prepared (as others have said, use a moving company), but you can also
rent the ones for moving
refrigerators from a rental supply
company if they're just being used for insured transport, and not prepared to move a half-full rack.
If you have enough people to be working staggered shifts to get things done, make sure there's some overlap so people know what's really going on, and not just blindly following a checklist.
If you have cabinets and not two post racks, and the doors close cleanly without crushing cables, I'd probably try to leave as much cabled up as I could, other than what had to be pulled to lighten the top of the rack. (okay, the one time I disagree with what's already been said)
... and then plan on some
recuperating time. Thanks to long days preparing for it as management only giving us two weeks notice (which they had known about for months, just didn't bother telling the sysadmins), our
Xyplex going out, and spending hours
in the machine room having to shout
over the fans of the two EMC
cabinets, I got sick and was out for
a week. It'd probably also be worth holding back a sysadmin or two on Sunday, so they'll be fresh to work on Monday dealing with whatever trouble tickets come in from the users.
addition:
So, after doing another move, a few things to consider:
If you're going to be moving during a cold time of the year, insist that the moving company bring a heated truck, and won't leave stuff out on a cold loading dock where you'll have sudden thermal change that might crack solder joints. (we moved mostly full racks, and wrapped them in bubble wrap and moving blankets to insulate them)
check on the size of the truck the moving company's going to use, so they don't bring something too large than can easily get to your loading dock.
place cones or other items the night before to make sure that no one decides to park where they'd impact the ability for the semi that the moving company brought from being able to get to the loading dock.
if one of the hardware vendors insists on bringing in their own moving truck, and having a packing crate delivered to move the rack in advance, ask them if their moving company is planning on bringing in a truck that can handle items as tall as their crate. (luckily, we were only moving within our campus, so they relented to letting the rack move uncrated)
if you have strange requirements (like the ramp for the raised flooring extends through the doorway, and some of the racks are too tall to make it through the doorway if the ramp's in place) make sure to get the actual people who are going to do the packing up of the racks to come and survey the situation, not just the manager. (we lucked out, as they were moving a machine room on the floor above a week before us ... so we happened to find that the way they were planning on lifting the racks down from the raised floor wasn't going to work, so two of us tore out a section of the raised floor before the day of the move)
|
|
|
answered Aug 5 '09 at 15:32
|
|