4

We placed a EATON Ellipse Max 1500 (900W) as the UPS for our HP Proliant ML350 G6. Upon first power failure (actually we only moved the UPS' input plug to a different socket), server immediatelly turned off, and the Health LED turned red and started blinking. UPS was in operation for about a week before that, with battery fully charged to 100%. Since our server's hot-plug supply is 460W, we are pretty sure we haven't overloaded it, the server was completely idle at that time (no web or win apps running except Windows Server core services).

Then we tried to do the same with a different, no-name older PC (Core 2 Duo, 2Gb RAM) with a generic power supply (not sure what the power is) and it continued working when we pulled the plug out. UPS load was less than 15% (measured in the provided Eaton utility).

We measured the UPS' output voltage using a smart oscilloscope and the THD of the UPS output waveform turned out to be 40%.

Did you have similar experiences? Could this be a faulty UPS? Or a faulty power supply? Or some HP sensors configured to trigger too strictly?

I wouldn't like replacing this UPS with the same brand, to get same results.

[Edit]

I also tried to do this while the server is turned off. While the UPS is working on battery, server will not start - as soon as I press the power button, Health LED starts blinking red.

6 Answers 6

9

I've seen this before and it's come down to the newer power supplies do not like the less expensive UPS systems.(it's not just HP) These new power supplies can detect fluctuation of 3ms and I've seen the UPS's response times to be from 3-5ms (on the low end). If you want to stay with Eaton try the PowerWare 9130

4
  • I am up voting this question and answer, I want to see if this is the case. I have never used an Eaton UPS and will probably stay away from them going forward. Nov 9, 2010 at 14:16
  • 2
    I've seen this as well with cheaper UPS's and HP servers. I read somewhere it has something to do with the output and sinewaves, I'm sure someone with an electrical engineering background could say more. Nov 9, 2010 at 14:41
  • 2
    It is probably related to the shape of the output waveform, rather than response times (if what you you consider by response time is time needed to switch over to batteries), because server doesn't even want to turn on while the UPS is on battery supply, with Health LED blinking red. As soon as I plug the UPS input cable back in, the server can be started and Health LED goes green. Since RMS of the wave is ok, I can only conclude that the problem is with the waveform (which has a THD of 40%).
    – vgru
    Nov 9, 2010 at 20:39
  • I can confirm this answer worked for my G7, did the test with both "online" (0ms transfer time) and regular UPSs and only the online worked as desired.
    – DarkCygnus
    Feb 26, 2019 at 16:44
4

There could be multiple problems here. Assuming your server was not plugged into any "surge protection" (non-UPS) plugs on the UPS.

1. Your power supply could have a defect and poor hold up time. If this is the case, it cannot survive the 3-5 mS that it takes a typical UPS to switch over to batteries. Hold Up time should be around 15mS or more.

2. The power supply's Power Factor Correction (PFC) might not be compatible with the "Modified Sine Wave" output of the UPS. I'll explain how this happens.

A typical UPS output looks like a square wave, with positive and negative components, and a short zero component in between. Exactly how the UPS matches the equivalent power of a true sign wave is up to the implementation. For example, it could hold a lower voltage of +/- 90V for a longer step time, or a higher voltage of 100V for a shorter step time. The average delivers the wattage advertised, assuming all is working to spec.

Modern PFC power supplies draw power at the top(bottom) of each sine wave, so as to draw less current than old-style transformer power supplies that draw large current amounts during the low voltage portion of the sine wave (leading and trailing edges). If the voltage of UPS "modified sine wave" is not high enough, some modern power supplies just don't see the "top" of the "sine wave" and shut off. So, the UPS is delivering the power, but the Power Supply is just not seeing it.

If you don't have the equipment to discern the problem, call HP and Eaton each and ask them if the other equipment is qualified to work together.

2
  • We can exclude the first problem, because the server didn't even want to start after the UPS had already switched to battery. Regarding the second issue, the signal indeed looks exactly like that: a square wave with voltage zero for a while (between positive/negative transitions), while its true RMS corresponds to that of a utility socket. But the statement about PS drawing power at the top is not exactly true: PFC supplies merely take care to charge the DC capacitors in sync with the input voltage, in order to keep the power factor low. They shouldn't care about the peak voltage value IMO.
    – vgru
    Nov 9, 2010 at 16:56
  • They SHOULDN'T care. BTW THD on a square wave is pretty meaningless if the meter is expecting a sine wave, it could be a very clean square wave but the meter is trying to compare it to the sine and marking all deviance as distortion. If you truly have Harmonics, interharmonics, notching, RF noise, frequency variations, etc. in the 40% range, that would be an instant RMA on the UPS, it is defective.
    – kmarsh
    Nov 10, 2010 at 20:41
3

We´ve got the same Problem with a APC Smart UPS SC1000. It´s a Problem with the HP Powersupply it is too sensitive and the server turns off when the power changeover happens. Now we changed the UPS to a Eaton 9130 and now it is properly working.

4
  • Thanks for the info. Datasheets for all the "enterprise-level" UPS devices we've considered state they produce "pure sinewave output", while with low-range devices this is not the case.
    – vgru
    Jan 11, 2011 at 9:25
  • 1
    I tested my DL360 G6 server with a pure sine wave APC UPS (SU620NET) and it powers off immediately when the power strip between the line input on the UPS and the wall socket is disconnected. The server also will not power on when the UPS is on battery, so the transfer time isn't the issue. When talking with APC they suggested a double-conversion UPS like the SRT1500XLA, which are very expensive. Jun 26, 2017 at 18:05
  • 1
    @SteveBonds: after switching to HP T1500 G3 UPS, we didn't have problems anymore. I believe the T1500 is not so expensive as double-conversion UPS's. If the server won't power on, I would say the "pure sine wave" is either not pure enough, or the battery is dead?
    – vgru
    Jun 26, 2017 at 18:37
  • The output of the SU620NET is likely to be very similar to the SU700NET mentioned here: hardwareinsights.com/database-of-ups-output-waveforms/2/… Thanks for the suggestion about the HP T1500. This makes sense as the R1500 is listed as the only UPS compatible with the DL360 on the HPE website. Jun 27, 2017 at 5:58
1

You should not "disconnect" a UPS from the wall plug while it is online carrying the critical load. Doing so remove any Neutral and/or Grounding reference and it may (or may not) causes problems depending on UPS or Load type. Read user manual.

1
  • In other words, the UPS won't provide uninterruptible power supply unless it's plugged into the mains socket?
    – vgru
    Oct 9, 2016 at 16:25
1

It's the "approximated sine wave" that the HP Gen6 servers don't like.

1
  • 2
    Supporting documentation?
    – Magellan
    Jul 26, 2018 at 0:18
0

I assume your power supply is an HP 460W CS HE Gold Power Supply. Either way all HP hotplug supply's are redundant, that means two actual units inside the supply so 460+460=920, and it is just barely overloading your UPS. If you tested the UPS on other PC's this definitely what the problem is. Plus your description sounds like every overloaded UPS I have ever seen. Try a 1000W UPS I'm 99% sure that will work for you.

2
  • 2
    No, we only have a single 460W power supply, no redundancy. Second socket is empty. Nevertheless, rated power is the maximum power that a supply unit can draw during a longer period of time. It does not correspond to the power actually being drawn from the network when the server is idle (Eaton utility shows around 10% load when the server is online).
    – vgru
    Nov 9, 2010 at 14:25
  • I stand corrected, according to the HP site they do make a 460W single. I wasn't able to find it before, sorry. Nov 9, 2010 at 14:54