1

How can I measure the power usage of a Dell Poweredge server from the command line interface?

5
  • Although most question with this size is VLQ, imho this isn't.
    – peterh
    Nov 13, 2015 at 9:41
  • @peterh Would you care to elaborate, so that I may learn to contribute in a better way?
    – Onnonymous
    Nov 13, 2015 at 13:53
  • Most review has only a short time to evaluate a post. So, it is much better if your post isn't only valid, but it also seems valid. One of them is if it is enough long, and it has a clear structure. When I ask, I ask always in at least in 3-4 lines, in most cases I try to answer the "Why do you want this to know?" question as well.
    – peterh
    Nov 13, 2015 at 21:35
  • 1
    I fail to understand why you think length or format of the question has anything to do with its validity. It's just a simple question, so I don't see a reason to waste any more words on it. I needed to find out this information because next year I need to move 25 PB (yes, petabyte) of storage hardware to another data center. As a preparation, we're checking if the system reported power usages matches the datacenter reported power usage. A Google search did not provide a simple recipe and I spent some time figuring it out, so I decided to provide a recipe to others to be helpful.
    – Onnonymous
    Nov 13, 2015 at 23:10
  • I tried to help, if you won't it, then I wish you many luck in the future.
    – peterh
    Nov 14, 2015 at 19:26

3 Answers 3

2

Install the srvadmin-all package and dependencies following these instructions: http://linux.dell.com/repo/hardware/latest/

You may need to log out and in to set the $PATH correctly.

Then:

[root@poweredge ~]# omreport chassis pwrmonitoring
Power Consumption Information

Power Consumption
Index             : 2
Status            : Ok
Probe Name        : System Board Pwr Consumption
Reading           : 126 W
Warning Threshold : 896 W
Failure Threshold : 980 W

Amperage
PS1 Current 1 : 0.6 A
PS2 Current 2 : 0.2 A

Power Headroom
System Instantaneous Headroom : 766 W
System Peak Headroom          : 549 W

Power Tracking Statistics
Statistic               : Energy Consumption
Measurement Start Time  : Wed Oct 17 20:18:51 2012
Measurement Finish Time : Fri Nov 13 09:51:52 2015
Reading                 : 3041.1 kWh

Statistic              : System Peak Power
Measurement Start Time : Wed Oct 17 20:18:51 2012
Peak Time              : Tue Jun  2 10:42:27 2015
Peak Reading           : 351 W

Statistic              : System Peak Amperage
Measurement Start Time : Wed Oct 17 20:18:51 2012
Peak Time              : Wed Aug  5 07:09:49 2015
Peak Reading           : 1024.2 A
1

In my case omreport chassis pwrmonitoring was maybe not giving the result I wanted.

Tested in 2021 on Proxmox 7

Working way to get

racadm get system.Power.Realtime.Power
racadm get system.Power.Realtime.Power
56 W | 191 Btu/hr

More data

racadm get system.Power
#Avg.LastDay=58 W | 198 Btu/hr
#Avg.LastHour=58 W | 198 Btu/hr
#Avg.LastWeek=57 W | 195 Btu/hr
#EnergyConsumption=25.455 KWh | 86878 Btu
#EnergyConsumption.Clear=******** (Write-Only)
#EnergyConsumption.StarttimeStamp=Sat Jul 03 17:05:13 2021
HotSpare.Enable=Enabled
HotSpare.PrimaryPSU=PSU1
#Max.Amps=0.7 Amps
#Max.Amps.Timestamp=Sat Jul 17 23:40:46 2021
#Max.Headroom=731 W | 2495 Btu/hr
#Max.LastDay=99 W | 338 Btu/hr
#Max.LastDay.Timestamp=Thu Jul 22 23:35:53 2021
#Max.LastHour=86 W | 294 Btu/hr
#Max.LastHour.Timestamp=Fri Jul 23 19:20:05 2021
#Max.LastWeek=152 W | 519 Btu/hr
#Max.LastWeek.Timestamp=Sat Jul 17 23:41:23 2021
#Max.Power=169 W | 577 Btu/hr
#Max.Power.Timestamp=Mon Jul 19 05:02:47 2021
#Max.PowerClear=******** (Write-Only)
#Min.LastDay=54 W | 184 Btu/hr
#Min.LastDay.Timestamp=Thu Jul 22 20:24:57 2021
#Min.LastHour=54 W | 184 Btu/hr
#Min.LastHour.Timestamp=Fri Jul 23 19:00:05 2021
#Min.LastWeek=53 W | 181 Btu/hr
#Min.LastWeek.Timestamp=Fri Jul 16 19:57:31 2021
PFCEnable=Disabled
#Realtime.Amps=0.2 Amps
#Realtime.Headroom=837 W | 2857 Btu/hr
#Realtime.Power=63 W | 215 Btu/hr
#RedundancyCapabilities=Not Redundant,Input Power Redundant
RedundancyPolicy=Not Redundant

Deprecated way

racadm getconfig -g cfgServerPower
root@pve:~# racadm getconfig -g cfgServerPower
# cfgServerActualPowerConsumption=65 W | 222 Btu/hr
# cfgServerPeakPowerConsumption=169 W | 577 Btu/hr
# cfgServerPeakPowerConsumptionTimestamp=Mon Jul 19 05:02:47 2021
# cfgServerPowerConsumptionClear=******** (Write-Only)
# cfgServerPowerLastHourAvg=58 W | 198 Btu/hr
# cfgServerPowerLastDayAvg=58 W | 198 Btu/hr
# cfgServerPowerLastWeekAvg=57 W | 195 Btu/hr
# cfgServerPowerLastHourMinPower=54 W | 184 Btu/hr
# cfgServerPowerLastHourMinTime=Fri Jul 23 18:58:59 2021
# cfgServerPowerLastHourMaxPower=86 W | 294 Btu/hr
# cfgServerPowerLastHourMaxTime=Fri Jul 23 18:50:01 2021
# cfgServerPowerLastDayMinPower=54 W | 184 Btu/hr
# cfgServerPowerLastDayMinTime=Thu Jul 22 20:24:57 2021
# cfgServerPowerLastDayMaxPower=99 W | 338 Btu/hr
# cfgServerPowerLastDayMaxTime=Thu Jul 22 23:35:53 2021
# cfgServerPowerLastWeekMinPower=53 W | 181 Btu/hr
# cfgServerPowerLastWeekMinTime=Fri Jul 16 19:40:13 2021
# cfgServerPowerLastWeekMaxPower=152 W | 519 Btu/hr
# cfgServerPowerLastWeekMaxTime=Sat Jul 17 23:41:23 2021
# cfgServerPowerInstHeadroom=835 W | 2850 Btu/hr
# cfgServerPowerPeakHeadroom=731 W | 2495 Btu/hr
# cfgServerActualAmperageConsumption=0.2 Amps
# cfgServerPeakAmperage=0.7 Amps
# cfgServerPeakAmperageTimeStamp=Sat Jul 17 23:40:46 2021
# cfgServerCumulativePowerConsumption=25.443 KWh | 86837 Btu
# cfgServerCumulativePowerConsumptionTimeStamp=Sat Jul 03 17:05:13 2021
# cfgServerCumulativePowerClear=******** (Write-Only)


RAC1168: The RACADM "getconfig" command will be deprecated in a
future version of iDRAC firmware. Run the RACADM 
"racadm get" command to retrieve the iDRAC configuration parameters.
For more information on the get command, run the RACADM command
"racadm help get".
1
  • 1
    Nice alternative way. Thanks!
    – Onnonymous
    Jul 27, 2021 at 13:28
0

This works on by Dell Poweredge T620 running Debian 10:

ipmitool dcmi power reading

Example output:

Instantaneous power reading:                   135 Watts
Minimum during sampling period:                 80 Watts
Maximum during sampling period:                465 Watts
Average power reading over sample period:      155 Watts
IPMI timestamp:                           20/08/23 05:02:42    UTC   
Sampling period:                          00000001 Seconds.
Power reading state is:                   activated
1
  • Another nice alternative way. Thanks!
    – Onnonymous
    Oct 25, 2023 at 13:33